Top Boiler Treatment for Intermittent Systems
This was a run around the bend dealing with a boiler that is not fired 24-7, even with 170F standby.
I have after some extreme effort and about 4 different combinations tried found the one that works and its looking pretty good. The chemical is Power Engineering 2478 which is a Nitrite and Amine. You set to 800-1200 PPM and monitor the other parameters within similar ranges to what is typically expected. This has gotten what would otherwise be considered a runaway corrosion problem into control. I can recommend it most likely for any distillery boiler that is not run often and is subject to go cold. A standby aquastat circuit on the boiler is advised, but the envelope may be able to be pushed. Your blowdown water should be near clear. The other thing I strongly advise is if you have extra Boiler capacity, then use your steam boiler to heat all your plant process hot water by one of several HX means. Then your system will be kept active most all the time, and your return station will stay warm which is important. Steam boilers of course do better when they are run near continuous. I have used and run Tube bundles with pump setups. Tube bundles in tanks, and HLT systems.